EdgeLink can work as IEC-61850 Server to exchange data with IEC-61850 Client of HMI/SCADA. Purchase and activation

Here will explain the application of IEC-61850 Server in detail.

  • In the menu tree on the left, expand "Data Service" and double-click on the "IEC-61850" item.

  • Enter the IEC-61850 configuration interface.

Configure the Communication parameters in the ICD file,SubNetwork-name、ConnectedAP-apName and Address

Configure IEC-61850 Service​

  • Check the "Enable 61850 Service" option.

General Settings​

This configuration page is used to specify general IEC-61850 server options, including:

  • Port
    Port number used to accept connections with IEC 61850 client (MMS). The default port number is 102.
  • Maximum Connections
    Specify the maximum number of supported connections. The default setting is 10.
  • IED Name
    The name of the current IED. You can change the name of the IED.
  • Enable Security
    Set the authentication mode for the IED. By default, the authentication mode is set to 'none'. Check the 'Enable Authentication' option to change the authentication mode to password.
  • Enable GOOSE
    Specify whether GOOSE service is supported. By default, GOOSE service is not enabled.

Configure IEC-61850 Service​

The IEC-61850 service currently supports two types of services: MMS and GOOSE. Please enable them as needed.

Configure SCL​

On this page, users configure the IEC-61850 model, datasets, and reports. During project compilation, an ICD file based on the SCL language will be generated.

It is important to note that the IEC-61850 service in EdgeLink only supports one IED from a single ICD file, and this IED can contain multiple LDevices. Configuration for this single LDevice is done in the "SCL View". When the IEC-61850 service is enabled, this LDevice will be automatically created, along with its LN0 node and LPHD node.

  • Access the LDEVICE (Logical Device) configuration interface

    The interface displays a list of configured LDEVICE, supporting new, edit, and delete operations.

    LDevice Inst: Logical device name, the unique identifier of the logical device under the IED. Ensure that the LDEVICE name does not conflict with other logical devices under the same IED.

  • Associated Logical Node (LN)

    • Click the "Add LN" button

  • Select Logical Node Type

    Select from the predefined "Logical Node Type" list (e.g. MMXU: Multiphase Measurement Logical Node).

  • Configure Logical Node Attributes

Select Data Object (DO) and Data Attribute (DA)

  • Configure Tag data mapping

After adding LN, tags can be associated with configured data attribute (DA) nodes. Double click the "Tag Name" cell in the Data Attributes (DA) to select an existing Tag in the project.

Select the associated Tag and click the "OK" button.

  • Tag List

Tag List page lists all the data attribute (DA) that have been added, and users can easily associate tags with data attributes (DA) in the Tag List page. The Tag List page supports Excel import/export, allowing users to quickly associate data attributes (DA) with tags in Excel.

The content of exporting Tag List to EXCEL.

Configure DataSet​

In the IEC 61850 standard, a dataset is an ordered collection of data attributes (DA) in logical nodes (LN), used for efficiently organizing and transmitting critical information between devices (such as measurement values, status signals, control instructions, etc.). The dataset is the foundation for communication between MMS (Manufacturing Message Specification) and GOOSE (General Object Oriented Substation Events).

  • Enter the Data Set configuration interface

The interface usually displays a list of created datasets and supports new, edit, and delete operations.

  • Create a new DataSet

Click the "Add" button

Edit Data Set form will list the data attributes (DA) in all logical nodes (LN) included in the current LDEVICE.

Select Data Object (DO) or Data Attribute (DA)

Click the "OK" button to return to the Data Set configuration interface and view the created dataset.

Configure Report​

The IEC 61850 Report is used to send information such as data changes and status updates from the server to the client.

The IEC 61850 report is configured and managed through the Report Control Block (RCB).

  • Enter the Report Control configuration interface

The interface usually displays a list of created datasets and supports new, edit, and delete operations.

  • Create a new Report

Click the "Add" button

  • Edit Report

Report Control Block Configuration

ParametersDescriptions
NameName of the Report Control Block. This name is relative to the LN hosting the RCB, and shall be unique within the LN.
Report IDIdentifier for the Report Control Block. The report identifier field may be used by clients to distinguish between reports from various BRCBs.
Data SetThe name of the dataset to be sent by the Report Control Block.
IndexedIf true, the Report Control Block instance names are built from the supplied name, followed by an index number from 01 up to maximum 99. The maximum index value is set by "Report Enabled max".
Config RevisionThe configuration revision number of this Report Control Block. The attribute shall represent a count of the number of times that the configuration of the Dataset referenced has been changed.
BufferSpecifies if reports are buffered or not
Buffer TimeBuffer time. After the first event has occurred, this buffer time has to elapse for a Report to be sent.
Integrity PeriodThe integrity period for cyclic reporting in milliseconds. 0 implies no integrity report.
Report Enabled maxDefines the maximum number of report control blocks of this type, which are instantiated at configuration time in the LN (and then used online). The maximum value is 99
DescDescription text

Report Format Configuration

Additional information segments to be included in the configuration report.

ParametersDescriptions
sequence-numberIf true, the SqNum shall be included in the report.
report-time-stampIf true, TimeOfEntry shall be included in the report.
reason-for-inclusionIf true, ReasonCode shall be included in the report.
data-set-nameIf true, DatSet shall be included in the report.
data-referenceIf true, DataRef or DataAttributeReference shall be included in the report.
buffer-overflowIf true, BufOvfl shall be included in the report.
entryIDIf true, EntryID shall be included in the report.
conf-revisionIf true, ConfRev shall be included in the report.

Trigger condition Configuration

The trigger options determine when the Report will be sent.

Configure the required report triggering method (multiple choices), triggered when True.

ParametersDescriptions
data-changeA report or a log entry shall be generated due to a change of the value of the data attribute (dchg)
quality-changeA report or a log entry shall be generated due to a change of the value of the quality attribute (qchg)
data-updateA report or a log entry shall be generated due to freezing the value of a freezable attribute or updating the value of any other attribute. An updated value may have the same value as the old value (dupd)
integrityA report will be sent on the expiration of the integrity period. (IntgPd needs to be set, such as 1000ms)
general-interrogationCaused by setting the attribute GI of the BRCB to TRUE by a client

Click the "OK" button to return to the Report configuration interface and view the created report.

Configure GOOSE​

  • Preconditions

Enable GOOSE service, LDEVICE (logical devices), LN (logical nodes), and related DataSet have been configured.

  • Enter GOOSE List configuration interface

The interface usually displays a list of GOOSE that have been created, and supports new, edit, and delete operations.

Create GOOSE Control Block (GCB)

Click the "Add" button

Configure GOOSE message parameters

ParametersDescriptions
NameThe name identifying this GOOSE control block.
GOOSE IDA system wide unique identification of the application to which the GOOSE message belongs
Data SetThe name of the data set to be sent by the GSE control block
Config revisionThe configuration revision number of this control block
MAC-AddressLength is 6 Octets and contains the value of the destination Media Access Control (MAC) address to which the GOOSE message is to be sent. The address shall be an Ethernet address that has the multicast bit set TRUE.Address range assignments: Starting address (hexadecimal): 01-0C-CD-01-00-00 Ending address (hexadecimal): 01-0C-CD-01-01-FF
APPIDThe APPID is used to select ISO/IEC 8802-3 frames containing GSE Management and GOOSE messages and to distinguish the application association. The reserved value range for GOOSE is 0x0000 to 0x3FFF. A unique, source-orientated GOOSE APPID within a system is strongly recommended
VLAN-PRIORITYPriority of outbound messages. Range of values shall be limited from 0 to 7. Where 0 is lowest and 7 is highest priority
VLAN-IDThe virtual LAN identifier. Range of values shall be limited from 0 to 4095 (FFF)

ICD File Import and Export​

The configuration of IEC-61850 is mostly reflected in the ICD file, and here we provide the import and export functionality for the ICD file, allowing users to directly use the imported ICD file. However, when an ICD file contains multiple IEDs, only the configuration of the first IED will be imported.

The ICD file import and export functions include:

  • Import from DAQ
    Configure IED from ICD template.
  • Export to ICD file
    Export the current IED configuration to an ICD file.
  • Import from ICD file
    Import existing ICD file.

Click "Export to ICD file" button to export the configuration.
Click "Import from ICD file" button to import the ICD file that has been configured in other software. However, when there are multiple IEDs in the imported ICD file, only the first IED configuration will be imported.

Example of configuring MMS service​

  • Enter the IEC-61850 configuration interface

  • "Enable 61850 Service"

  • Add LN

  • Select Logical Node Type MMXU - (Measurement)

  • Select DO
    Note: The selected DO should include DA of Float or Double data type.

  • Associate tag with DA of Float or Double data types

  • Project Download

  • Test with client

Example of configuring GOOSE service​

In the IEC-61850 master station, configure the GOOSE model, including enabling GOOSE services, configuring bound physical network ports, configuring and defining GOOSE related logical nodes, datasets, and GOOSE control blocks.

  • Enter the IEC-61850 configuration interface

  • "Enable 61850 Service"

  • "Enable GOOSE", then set "GOOSE LAN"

  • Add LN

  • Select Logical Node Type MMXU - (Measurement)

  • Select DO
    Note: The selected DO should include DA of Float or Double data type.

  • Associate tag with DA of Float or Double data types

  • Create or select a Dataset

  • Add data objects to the GOOSE Dataset according to your requirements

  • Associate GOOSE control blocks (GoCB) with the Dataset

Add GOOSE control blocks (GoCB)

  • Set communication parameters for GoCB

Associate with a unique Dataset; Set communication parameters for GoCB, such as MAC address, application ID (APPID), etc.

  • Project Download

  • Subscribe to GOOSE through the client and test it

Import from DAQ​

Users can import configured points with 'Electrical Attribute' into the IEC-61850 service using the template.

  1. Click "Import from DAQ" button

  2. Select template. The default mapping between power attributes and IEC 61850 types in the template file is as follows::

    Power attributeLNodeDODA
    Power TelemetryGGIOIndmag-f
    Status SignalGGIOAnInstVal
    Control CommandGGIOSPCSOstVal
    Energy RecordMMTRSupWhactVal
    Protection SettingGGIOSetValsetMag-f

    Users can also modify the template file to change the IEC 61850 type associated with each power attribute.

  3. Select tags. By default, these points will be configured within a single LDevice. If "Merge into one LDevice" is unchecked, each meter will generate a separate LDevice containing only its own points.

  4. Configure limit on the number of tags for LNodes,Maximum Points per LNode, Each LNode has a configurable point limit. When the number of points for a given type exceeds this limit, the system automatically creates additional LNodes.

    Example Implementation: When importing 1,000 telemetering points with a 300-point limit per LNode:

    • The LDevice will contain 4 GGIO-type LNodes
    • The first three LNodes will each contain 300 Ind-type DOs
    • The fourth LNode will contain the remaining 100 Ind-type DO。

  5. Config

    • rptID Value:
      • Default: None (results in empty ReportControl id)
      • When "Report Index" is selected: {LDevice inst}/LLN0$RP${ReportControl name}
    • Report Enabled Max: Sets the maximum value for RptEnabled
    • Add Device Name as du Prefix:
      • When unchecked: Point's dU value = Point name
      • When checked: Point's dU value = [Device name] + [Point name]